downlights from 13 amp connection unit


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
Search this topic :: View previous topic :: View next topic  
Author Message
crooner

from United Kingdom

Joined: 15 Jan 2010
Posts: 65
Location: Glasgow,
United Kingdom

PostPosted: Fri May 28, 2010 6:35 pm Reply with quote

Hi, i want to fit down lights downstairs in kitchen ceiling, i have a 13 amp socket that will never be used as it is jammed behind a kitchen unit,i can get access to the cable's from the back quite easily,and fit connection unit higher up the wall for access, so can i change 13amp socket to a 13amp connection unit,then run a 1.5 cable to lights,
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
BigJon

from United Kingdom

Joined: 18 Jun 2006
Posts: 435
Location: Glasgow,
United Kingdom
Thanked: 24 times

PostPosted: Fri May 28, 2010 6:54 pm Reply with quote

I dont see why not, presuming its a switched fused connection unit your going to be fitting.
Will you be burying the cables, do you know if you have RCD protection on said circuit?
Back to top
The following user says thank you to BigJon for this useful post:
crooner (29 May 2010)
 Alert Moderators
crooner

from United Kingdom

Joined: 15 Jan 2010
Posts: 65
Location: Glasgow,
United Kingdom

PostPosted: Fri May 28, 2010 7:32 pm Reply with quote

bigjon, yes it is a switched fuse unit, i'm not sure if i have RCD protection the fuse box have switches,the cables run down to a 13 amp socket i was going to cut these cables and run to the fused connection unit,
from what i have read on this site this is okay if the fused connection unit was a spur, but i was unsure because it would be on the ring circuit as i cant get access to front of 13 amp socket, i can only get into the cables that go into the back of socket
Back to top
 Alert Moderators
spark1

from United Kingdom

Joined: 10 Aug 2009
Posts: 243
Location: Liverpool,
United Kingdom
Thanked: 16 times

PostPosted: Fri May 28, 2010 8:53 pm Reply with quote

would these downlights be 230 volt or 12 volt type ?
Back to top
 Alert Moderators
crooner

from United Kingdom

Joined: 15 Jan 2010
Posts: 65
Location: Glasgow,
United Kingdom

PostPosted: Sat May 29, 2010 12:15 am Reply with quote

Hi spark1, i was thinking of putting in 230volt they will go into plaster board ceiling which i will be getting plastered,(no more than 2 50 watt's plenty of room in ceiling,by the way i have decided to put a 13 amp socket above the one i cant access & just run a fused connection unit to lights,can you advise me on lights they are not for show,someone in the family is visually impaired
Back to top
 Alert Moderators
PrenticeBoyofDerry

from United Kingdom

Joined: 30 Jun 2009
Posts: 17392
Location: Londonderry,
United Kingdom
Thanked: 1734 times

PostPosted: Sat May 29, 2010 6:27 am Reply with quote

The 13 amp socket should not be jammed behind a kitchen unit, they should be easily accessesible. So if at any time they did need to be inspected and tested this could be done.
I suggest the socket is moved, so it is accessible.
A fused connection unit can be installed to this, you could use a switched FCU as this can then be used as a functional switch, if not you would need to then drop a switch cable down to operate the lights. The FCU would need to be down fused to a suitable rating.
When fitting downlights you must ensure that you have adequate ventilation around the fitting and that their use does not breech any fire regulations.
Back to top
The following user says thank you to PrenticeBoyofDerry for this useful post:
crooner (29 May 2010)
 Alert Moderators
wingcoax

from United Kingdom

Joined: 01 Mar 2009
Posts: 1915
Location: Blackpool,
United Kingdom
Thanked: 156 times

PostPosted: Sat May 29, 2010 11:39 am Reply with quote

What seems to have been missed so far is that you cannot use a 13A fuse on the lighting circuit. You will have to fit a 3A fuse in the FCU in order to comply with regs.
Back to top
The following user says thank you to wingcoax for this useful post:
crooner (29 May 2010)
 Alert Moderators
PrenticeBoyofDerry

from United Kingdom

Joined: 30 Jun 2009
Posts: 17392
Location: Londonderry,
United Kingdom
Thanked: 1734 times

PostPosted: Sat May 29, 2010 12:10 pm Reply with quote

wingcoax wrote:
What seems to have been missed so far is that you cannot use a 13A fuse on the lighting circuit. You will have to fit a 3A fuse in the FCU in order to comply with regs.
PrenticeBoyofDerry wrote:
The FCU would need to be down fused to a suitable rating.
icon_cool.gif
Back to top
 Alert Moderators
wingcoax

from United Kingdom

Joined: 01 Mar 2009
Posts: 1915
Location: Blackpool,
United Kingdom
Thanked: 156 times

PostPosted: Sat May 29, 2010 12:17 pm Reply with quote

PrenticeBoyofDerry wrote:
The FCU would need to be down fused to a suitable rating.
icon_cool.gif[/quote]
Sorry; reading too quick again. icon_rolleyes.gif
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
GU10 Downlights earth connection 5 820 Fri Apr 11, 2008 6:40 pm
Switched Fused Connection Unit + Oven 6 4060 Tue Jul 19, 2005 10:59 am
Fused connection unit within chiney hood? 3 660 Sat Jul 21, 2007 9:10 am
Consumer Unit to Supply final connection - who do I talk to? 26 1820 Fri Aug 05, 2005 8:53 am
Fused Connection Unit 10 1080 Mon Sep 19, 2005 11:11 am


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.