2 Showers
Reply with quote Thanks

I have a 9.5 kw shower currently, and want to add an additional 9.5Kw shower unit, after doing the calcs the consumer unit is not capable of running two showers at the same time. - Is there a way around this ?. Reading through the forum an interlock has been mentioned - are they any good ? - where can i get more information ? - Any ideas ?..Thanks icon_question.gif
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
Pens

from United Kingdom

Joined: 17 Jan 2006
Posts: 2433
Location: Kent,
United Kingdom
Thanked: 0 times

PostPosted: Wed Aug 16, 2006 9:33 pm    Post Subject:
Reply with quote Thanks

It may be possible. What size is your main incomer fuse?
Back to top
 Alert Moderators
breezer

from United Kingdom

Joined: 03 Jan 2003
Posts: 23346
Location: Sussex,
United Kingdom
Thanked: 5 times

PostPosted: Wed Aug 16, 2006 9:37 pm    Post Subject:
Re: 2 Showers
Reply with quote Thanks

stanmike wrote:
I have a 9.5 kw shower currently, and want to add an additional 9.5Kw shower unit, after doing the calcs the consumer unit is not capable of running two showers at the same time. - Is there a way around this ?. Reading through the forum an interlock has been mentioned - are they any good ? - where can i get more information ? - Any ideas ?..Thanks icon_question.gif


interlock means only one shower at a time can run.

the other thing to consider is water pressure, you may not have enough to run 2 showers at same time

__________________
Do you like music Mr Finch?
Forum = Opinions
Back to top
 Alert Moderators
ebee

from United Kingdom

Joined: 14 Aug 2005
Posts: 1067
Location: Lancashire,
United Kingdom
Thanked: 0 times

PostPosted: Thu Aug 17, 2006 5:08 am    Post Subject:
Reply with quote Thanks

The only way I can see an interlock is one or two contactors/mains relays monitoring the heating element voltage on the showers(s) unless a simple manual DP changeover switch is used .
any different ideas?
Back to top
 Alert Moderators
Pens

from United Kingdom

Joined: 17 Jan 2006
Posts: 2433
Location: Kent,
United Kingdom
Thanked: 0 times

PostPosted: Thu Aug 17, 2006 4:23 pm    Post Subject:
Reply with quote Thanks

He could use a Castell interlock on the shower room doors icon_rolleyes.gif

Joking aside, if the incomer is 100amp with a few switchgear changes (assuming there is enough mains pressure) there should not be a problem


Last edited by Pens on Thu Aug 17, 2006 4:26 pm, edited 1 time in total
Back to top
 Alert Moderators
Spark123

from United Kingdom

Joined: 02 Jun 2005
Posts: 10887
Location: Cumbria,
United Kingdom
Thanked: 39 times

PostPosted: Thu Aug 17, 2006 4:26 pm    Post Subject:
Reply with quote Thanks

Pensdown wrote:
He could use a Castell interlock on the shower room doors icon_rolleyes.gif


icon_eek.gif icon_lol.gif
Back to top
 Alert Moderators
Adam_151

from United Kingdom

Joined: 17 Jun 2004
Posts: 4538
Location: United Kingdom
Thanked: 10 times

PostPosted: Thu Aug 17, 2006 7:33 pm    Post Subject:
Reply with quote Thanks

Yeah if 100A fuse, then I'd put a fair bet on it never blowing in practice, though I'd be tempted to put it on a separate CU, to avoid stressing the incommer and bus bars

[I'd have thought, like cables, CUs would be built with 1.45 x design current for conventional time built in, and you are not going to be exceeding the design current of a modern CU for anywhere near that time unlesss you want to use both showers at once for quite a while, all the while space heating the garden/growing pot in the attic/working on quantum physics with your particle accelerator]
Back to top
 Alert Moderators
stanmike

from United Kingdom

Joined: 16 Aug 2006
Posts: 2
Location: United Kingdom
Thanked: 0 times

PostPosted: Thu Aug 17, 2006 9:18 pm    Post Subject:
2 shower
Reply with quote Thanks

mains incomer is 100A, plenty of mains water pressure. I could add a c/u for the shower but still think that over all load ( taking diversity into account ) is too great for the supply.
Back to top
 Alert Moderators
tommo2

from Ireland

Joined: 04 Jul 2006
Posts: 26
Location: Ireland
Thanked: 0 times

PostPosted: Fri Aug 18, 2006 3:39 am    Post Subject:
Reply with quote Thanks

Any good wholesaler will sell you the interlock gear so that only one shower is on at one time.
There are 2 types:
1. Priority- a pullcord switch in the main bathroom controls a changeover contactor, which energises shower in main bathroom and de-energises shower in other room. Main disadvantage is anyone in the main bathroom can turn off your other shower without warning. Also, if they leave their pullcord on, then you will have no shower. It is fairly cheap though (around #50 for materials).

2. Non-priority - both showers have their own dedicated contactors which are interlocked. Whichever shower is operated first stays energised until it is turned off. (sort of like first come first served). The other shower cannot be turned until the other is finished. Around 150 for materials.

__________________
Pull up the handbrake and walk away
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16480
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Fri Aug 18, 2006 8:37 pm    Post Subject:
Reply with quote Thanks

Pensdown wrote:
It may be possible. What size is your main incomer fuse?


Not even if main fuse is 100A.

Consumer units do not support more than one breaker of 40A capacity or greater.

__________________
As George Michael once said, "..if you're gonna do it, do it right, right?"
Back to top
 Alert Moderators
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 12845
Location: Yorkshire,
United Kingdom
Thanked: 21 times

PostPosted: Fri Aug 18, 2006 9:50 pm    Post Subject:
Reply with quote Thanks

securespark wrote:
Pensdown wrote:
It may be possible. What size is your main incomer fuse?


Not even if main fuse is 100A.

Consumer units do not support more than one breaker of 40A capacity or greater.

not even a 3-phase board converted to single phase? icon_wink.gif
Back to top
 Alert Moderators
Adam_151

from United Kingdom

Joined: 17 Jun 2004
Posts: 4538
Location: United Kingdom
Thanked: 10 times

PostPosted: Fri Aug 18, 2006 9:57 pm    Post Subject:
Reply with quote Thanks

securespark wrote:


Consumer units do not support more than one breaker of 40A capacity or greater.


Thats something I've heard branded aout a few times, but I've yet to see anything to that effect in the technical data putout by CU makers, maybe its legend that dates from when wylex standard boards had one 45A position and carries onto this day and refuses to die?

I must admit I can't see the physics of it myself, if any way could have a 50A breaker, then each tab on the bus must be rated to 50A, the backbone of the bus must be rated to carry 100A, so I really cannot see what the difference is between 2x showers on 2 x 40A breakers and 4 x20A ovens on 4 x 20A breakers
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16480
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Fri Aug 18, 2006 11:02 pm    Post Subject:
Reply with quote Thanks

Think it was GE. Def read it in someone's prod lit...

Think about it. Two showers pulling 80A. A cooker, a ring or 3. Won't be long before 100 could be exceeded...

__________________
As George Michael once said, "..if you're gonna do it, do it right, right?"
Back to top
 Alert Moderators
Pens

from United Kingdom

Joined: 17 Jan 2006
Posts: 2433
Location: Kent,
United Kingdom
Thanked: 0 times

PostPosted: Sat Aug 19, 2006 1:31 pm    Post Subject:
Reply with quote Thanks

Pensdown wrote:
Joking aside, if the incomer is 100amp with a few switchgear changes (assuming there is enough mains pressure) there should not be a problem


I'm with Adam, I also can't see problem even if it means fitting another small CU via some henley blocks
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
how to wire 2 electric showers on the same circuit 11 860 Fri Aug 17, 2007 8:41 pm
Renew showers kw?? 3 340 Sun Jul 22, 2007 11:08 am
Showers! 6mm T&E cable to be used for shower 6 860 Sun Aug 19, 2007 10:11 am
2 electric showers 2 300 Fri Aug 24, 2007 11:18 am
mira showers 6 320 Mon Dec 10, 2007 6:12 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.