Are LAP products any good? e.g.
http://www.screwfix.com/p/lap-50a-dp-ceiling-pull-cord-switch-white/7251g
45A or 50A switch will be satisfactory.
9.5kW is just under 40A.
He almost certainly is not, at least not in the way that you think he is.Hate to **** on your parade but your incorrect,
How do you know that he was wrong to at least start with using 240V? Are you unaware of how common it is for shower manufacturers to use a headline figure for their product's performance at 240V?I assume you erroneously calculated using 240V
Actually it became BS 7671 very early in the life of the 16th.but you should, as per BS7671 (In fact as per the 15th and 16th Editions of the IEE Regs - Before it became BS7671)
Only if 9.5kW is the load of the appliance at 230V. It almost certainly is not. The most likely figure for the load at the official U0 is about 38A.the correct voltage for design calculations is 230V and for a 9.5kW load that is 41.3A, as such all cable calcs etc should be based on this.
So is the length of the cable.Everyone here is giving out advice, yet no-one has asked the obvious questions...what size is the supply cable and how far is it from the Consumer unit...very important when installing items of equipment, especially with significant loads..The Switch and the MCB are irrelevant to a cable burning out.
I nearly added a warning in my reply to alert you to the possibility of yet more tedious b****cks from Winston, who, basically, is simply too thick to understand what the word "nominal" means.the correct voltage for design calculations is 230V.
We have all had to put up with his ignorant drivel for years - sadly he won't stop because he is also too thick to realise that he is wrong.
No - that's more TAS delusion on your part.Actually more intelligent than you.
If an item is rated at x kW at 240v then these are the figures you use to calculate current. IF you than use it on a 230 v supply it is a simple matter to work out the current taken at 230 v.
Problem is no one in the UK has a 230 v supply, as you will notice if you actually measure it.
How do you know that he was wrong to at least start with using 240V? Are you unaware of how common it is for shower manufacturers to use a headline figure for their product's performance at 240V?.I assume you erroneously calculated using 240V
Actually it became BS 7671 very early in the life of the 16th..but you should, as per BS7671 (In fact as per the 15th and 16th Editions of the IEE Regs - Before it became BS7671)
Only if 9.5kW is the load of the appliance at 230V. It almost certainly is not. The most likely figure for the load at the official U0 is about 38A..the correct voltage for design calculations is 230V and for a 9.5kW load that is 41.3A, as such all cable calcs etc should be based on this.
Totally irrelevant. The unit is rated at 9.5kW and the supply voltage has a NOMINAL rating of 230V, thus to comply all calculation must be based on these figures and not one you pick out of your head to try to win an argument with yourself...![]()
Good advice. You may care to follow it.I suggest that you stop arguing over something where you will lose every time as it will save everyone the hassle and stop ****y posts![]()
The problem is you clearly do not understand what you are talking about in this context. The supply voltage for the UK has a NOMINAL rating of 230V..that means all design calculation should be undertaken using this voltage. It of irrelevant what you measure with your B&Q kill you quick ****y Chinese made multimeter Winston. If I take a random measure of the properties where I live I can hazard a guess most will come in at 238.6V as an AVERAGE that will fluctuate over the course of a day.
Now if I go into the buildings I manage and take a measure...Low and behold, the majority will be at 230V as it is stabilised by UPS systems and other line attenuation equipment...so, as the Regs clearly stat 230V, I suggest that you stop arguing over something where you will lose every time as it will save everyone the hassle and stop ****y posts![]()