Morning all,
Mulling over options for rewiring sockets in a room where the 2 external walls will be internally insulated (100mm solid stuff). This isn't a new circuit so (unless I've misread the regs) not notifiable- however I would like to do it correctly.
At the moment, 2.5mm T & E cables are under the timber floor then chased 300mm up the wall into backboxes. Underfloor is accessible so I can replace cable where necessary rather than joint it (to get the extra length since the sockets are going to be 125mm at least away from the masonry wall)
Question is how exactly to apply the derating factors in table F2 (Onsite Guide BS 7621) if I just push the cables through the insulation. There will be 4 sockets in that part of the ring where cabling would pass through insulation- does that mean I need to consider the ring having passed through 800mm of insulation (so derate to 50%) or do I instead consider that each single cable has passed through 100mm of insulation so derate that single cable to 78%?
I'd prefer to use the above method (one big advantage is it keeps the cables at least 100mm away from the wall surface so pretty safe from future fixing attempts) but not if it means using 6mm T & E to overcome the derating effect of the insulation.
Plan B does exist- bring cables up through floor just behind skirting board and up the front face of the insulation so that it is in contact with the plasterboard (Method 102).
And Plan C also exists- use 4mm T & E in conduit through the insulation for those sockets affected, reduce back down to 2.5mm at sockets not affected by insulation (on internal walls)
All advice appreciated (except the one about insulate externally- can't in these 2 rooms, only 100mm between my place & next door!). Oh yes, the CU is fairly modern split load with RCD on both sides so that bit is covered.