Recent content by D_Hailsham

  1. D

    How to size panel rads to allow boiler condense

    Condensing boilers are designed to work with a flow/return temperature difference of 20C. The return temperature needs to be below 55C for condensing to occur (the lower the temperature, the greater the condensing). The current "official" recommendation is to set the flow temp of a condensing...
  2. D

    install shower in wooden building

    The forume has changed since I last used it. To carry on from where I was ... The company making and installing the annexe does not do plumbing, so that's up to us. There will be a small bathroom with toiler, hand-basin and shower. My question concerns the instalation of the shower, Here is...
  3. D

    install shower in wooden building

    We are having a custom-built annex, made of wood, installed in the back garden.
  4. D

    TBSE on a very long radiator

    You say that, but BS EN442 requires rads to be tested using TBSE. It, allegedly, gives 2% more output compared to BBOE.
  5. D

    Best way to heat small building

    Thanks for all the suggestions; there's plenty to think about. I had already discounted storage heaters for the reasons given by SimonH2. I was not aware that oil filled radiators took longer to heat the space. I don't know if that is significant as most of the heating up will be done before...
  6. D

    Extension - seconded zoned gas boiler

    Whoever designed your extension should have done a heat loss calculation for the original house and the house with extension. Do you have this information?
  7. D

    Best way to heat small building

    Does it make any difference if they are oil filled or fan driven convector heaters?
  8. D

    Best way to heat small building

    The building is single storey detached, built in the 1970's, and has electricity only - no gas. It is about 8m square, divided into several rooms. It will be used for sales and as offices. What is the best way of heating the building? It will only be used in the daytime - say from 8am to 9pm.
  9. D

    Reverse Circulation

    Have you passed the £1240+VAT problem over to your insurance company? It's their job to sort everything out, not yours.
  10. D

    Bypass Valve Setting on a Mult-zone setup

    A bypass is not intended as a stand-by, in case a motorized valve fails. Provided you buy a decent valve, e.g Honeywell (not an Asian look-a-like) you should get many years of life out of them. Your boiler does have an internal bypass, but it's mainly there to regulate the pump output. (See the...
  11. D

    Bypass Valve Setting on a Mult-zone setup

    Do you mean the Ecofit Pure 830?
  12. D

    Cylinder Bypassed

    Can you post a pic of the pipework - not just the tee joint?
  13. D

    I have incorrectly wired my replacement programmer (ed)

    How doyou know that the Danfoss fault was not caused by the backplate? Have you checked that there are no strands of wire touching an adjactent terminal? I would change the backplate for a start. (Assuming you got one with the ST9400) TURN POWER OFF AT MAINS FIRST Write down which wire...
  14. D

    HW/CH flow and system type

    You seem to be talking about the old version of X800. Check out the FAQ's at X800.
  15. D

    Opentherm & Weather Comp Boilers

    So short that there is only one boiler listed; and that's a "liquid fuel" of a make I've never come across. I remember reading, a long time ago, that the OT Associationw were stopping testing boilers for compatibility, only testing controls. Weather comp is, obviously, not mentioned. There is a...