  1. P

    Boulters C2 Pathfinder.. Combustion

    So if I used the charts attached .. If the 62.7kw (214000btu) Im trying to get to would equal approx 2.00usg at 100psi would be the same as using a 1.65 nozzle at 145psi?
  2. P

    Boulters C2 Pathfinder.. Combustion

    Ive estimated the previous output was about about 61Kw using 1.95 usg/hr. If Adjusting the diffuser to fine tune the settings what should I be expecting if I adjust it up and down.
  3. P

    Boulters C2 Pathfinder.. Combustion

    Hi. Servicing an old Boulters C2 /9or 8 pathfinder. The plate on the side suggest original set up for gas oil . The sticker on the burner suggest the same but has since been written over on pen 28sec.. Burner is an old Riello R40 G10. Written on the burner sticker is 170 psi . nozzle...
  4. P

    camray 5 150/200 settings manual

    I have found a Boulters boilers commissioning data sheet, that lists most of the boulters boilers. Shows Models, KW, Head, nozzles, PSI, bar CO2 and flue temps. It also has data for class D gas oil.. It looks like the data I have to set it to is similar to that of the 51kw Class D gas oil...
  5. P

    camray 5 150/200 settings manual

    The flue gas temp is measured outside at the flue. It is a short run, 90deg out the top and straight through the wall . About 1mtr from top of boiler to test hole in the center of the flue. Balanced Flue
  6. P

    camray 5 150/200 settings manual

    Do you think the flue temp is unusually lower even with it only being 0.1 size off the lowest nozzle and with higher oil pressure. , If I change the nozzle to the 1.35 output, Should I also be looking for some another fault. ?
  7. P

    camray 5 150/200 settings manual

    Hi . I just serviced a Boulters Camray 5 150/200. I always first run it for a minute to check if it starts ok etc before I start and sounded ok. Quite a bit of carbon on the baffles, just presumed not seen a service in years. Nozzle and blast tube looked ok. Written in marker on the side...
  8. P

    Oil boiler on an ASHP designed system

    I have only done a few days service and install on ASHP course and feel I need to know more before venturing down that route. Client is adamant she does not want an ASHP now for some reason , It is just sitting there waiting to be plumbed in , she offered to sell it to me..? I have opted out of...
  9. P

    Oil boiler on an ASHP designed system

    I asked for some extra info from them to follow but have not heard back, so quite happy actually not to be the 4th plumber in a year. But good to learn on others design opinions. Would be more interested on how the tapstat / bypass from Johntheo5 set up works as I have a client grant boiler on...
  10. P

    Oil boiler on an ASHP designed system

    I did ask for the ASHP install design details but was told they had nothing ...
  11. P

    Oil boiler on an ASHP designed system

    Hi. I have a potential client that has all the radiators fitted suitable for an ASHP (but pump not plumbed in) now they want an oil boiler plumbed back in instead but want to keep all the big radiators , just in case they decide to change their mind As they still have the ASHP but not fitted. ...
  12. P

    Can someone explain Return Temps to me?

    I know a while back. but Im having the same dilema (44kw Boiler) . Did you find sort the issue? Did you find a blending valve for 50kw boiler. Or did the bypass with manual valve work?