Ihave a 415v step down TX with a secondary output of 110v.
The ZS for the incoming swa is 0.24.
The ZS for the outgoing 110v ccts is a lot lower is this correct?
Yes, that is correct because the secondary winding has a small impedance, however you need to calculate the equivalent short circuit current on the 110V side using data from the 415V (or whatever primary) side if you're to get the right figures to prove any protection you have in place will work.
Yes, that is correct because the secondary winding has a small impedance, however you need to calculate the equivalent short circuit current on the 110V side using data from the 415V (or whatever primary) side if you're to get the right figures to prove any protection you have in place will work.