There's a cable from the consumer unit to the garden shed (1.5 SWA cable) at a depth of 18 inches and running 25m long which runs a shed light operated by a pullcord switch.

I've got a spare rcd weather proof socket which I would like to install in the shed and possibly use the same cable.

I've been told if I use a 16A MCB in the consumer unit and a fused spur (with 3A or 5A fuse) installed in the shed for the light, it should be OK.

Does anyone know if this is right?

Thanks
 
Sponsored Links
There's a cable from the consumer unit to the garden shed (1.5 SWA cable) at a depth of 18 inches and running 25m long which runs a shed light operated by a pullcord switch.
What breaker is it on right now?


I've got a spare rcd weather proof socket which I would like to install in the shed and possibly use the same cable.

I've been told if I use a 16A MCB in the consumer unit and a fused spur (with 3A or 5A fuse) installed in the shed for the light, it should be OK.

Does anyone know if this is right?
 
OK - yes, you would need an FCU for the lights at the other end, and as I said changing the MCB is notifiable and really should not be done without checking that the existing cable is OK for voltage drop and above all fault-loop impedance.

If you read the information linked to above you'll see why.
 
Sponsored Links
on 25M run you will be way out of spec on volt drop.
 