No - I am not branching out into commercial/industrial...
I need to explain to someone why 3-phase volt-drop figures are (SQRT(3))/2 of the single phase ones. (I hope I'm right that that is what they are..... :? )
I'm sure that with time I could work it out (well, sort of maybe sure), or find a website showing the calculations, but don't have that time right now.
Can anybody help me, either with the calculations, or pointing me at a web resource?
mmm 3 phase
you'll have to tell me what you are and aren't changing between the single phase calcs and the 3 phase ones before your statement makes any sense.
for a given conductor size and conductor current and assuming balanced load a 240/415V three phase system will have half the P-N voltage drop of a 240V single ended single phase system as there is no neutral current.
Pick any multicore table in Appendix 4, and compare the VD for 2-core single phase and 3- / 4- core three phase....
Which of course is how we get to SQRT(3)/2 - if there was a neutral current the VD would be the single-phase figure x 1.732..., but with no neutral current it becomes S-P x 0.866....
Doh.
ahh thier figures are based on the drop in the phase-phase voltage
makes sense now.