Going to be installing the electrics to a steam cabinet later on, I have not seen the job yet.
Client informs me the load is 3kw with a seperate RCD, the load comes to 13 amps, has anybody installed one of these before and how is the load split up?
its only a power shower, so what do these take a 5amp spare if that, anyway i wont know the full SP till i get there, just lookin for pointers?
 
Sponsored Links
From a B16 MCB in the RCD side of the board, run a minimum 2.5.sq.mm cable to the outlet point, install a 13amp Switched FCU with neon, and run the flexible cable to the 13amp equipment to be supplied.
 
Thanks kai, just sorted the job before, between the switch and the load the manufacturer supplied an rcd which i fitted, the circuit boards were already fitted by manufacturer for computer
 