Hi all - newbie here with a problem...
Today I replaced the diaphragm on my Halstead Ace High combi boiler. All went well, I now have hot water again. It's the second time in 10 years I've done this, so not a virgin to the (non gas) side of the boiler.
HOWEVER - I now have no CH.
The CH was on for about half an hour after I powered up the boiler again this lunchtime - then went off, and hasn't been on since.
Going through some fault finding - I'm getting 230V across terminals 1&2, as expected and the CH thermistor is giving a reading of around 12K. This is as expected too? Odly though, if I disconnect the CH thermistor and power up the boiler, it ignites for about 10 seconds before shutting off again.
Does anyone have any other suggestions? I'd rather not shell out £200+ for a new pcb is there's another component I should be looking at first - or indeed have misunderstood the thermistor resistance, and it indeed is dead.
I should add that the DHW is working perfectly. The boiler fires up when hot water is drawn and it's piping hot. Just no CH.
I do have an external thermostat which controls the CH - that's clicking at around 14 degrees at the moment. It's been on the boiler for at least 5-6 years, and have no reason to suspect that's faulty.
Any other diagnostics would be greatly appreciated.
Many thanks
Today I replaced the diaphragm on my Halstead Ace High combi boiler. All went well, I now have hot water again. It's the second time in 10 years I've done this, so not a virgin to the (non gas) side of the boiler.
HOWEVER - I now have no CH.
The CH was on for about half an hour after I powered up the boiler again this lunchtime - then went off, and hasn't been on since.
Going through some fault finding - I'm getting 230V across terminals 1&2, as expected and the CH thermistor is giving a reading of around 12K. This is as expected too? Odly though, if I disconnect the CH thermistor and power up the boiler, it ignites for about 10 seconds before shutting off again.
Does anyone have any other suggestions? I'd rather not shell out £200+ for a new pcb is there's another component I should be looking at first - or indeed have misunderstood the thermistor resistance, and it indeed is dead.
I should add that the DHW is working perfectly. The boiler fires up when hot water is drawn and it's piping hot. Just no CH.
I do have an external thermostat which controls the CH - that's clicking at around 14 degrees at the moment. It's been on the boiler for at least 5-6 years, and have no reason to suspect that's faulty.
Any other diagnostics would be greatly appreciated.