adding new ring main

Joined
5 Jan 2004
Messages
25
Reaction score
0
Country
United Kingdom
Can i create a new ring by running a spur off an existing ring to a 30 amp MCB then use this as the \\\'consumer unit\\\' for a new ring?
 
Sponsored Links
The simple answer to your question is – definitely NOT!!. A spur can only supply a single socket outlet (the outlet itself may be single or double).

You have two options:
1. Extend the existing ring
2. Install a new ring protected by 32A MCB/RCD at the board,

The second being the better option.
 
thanks, i am in the middle of converting my loft, i will extend the ring from the floor below, it only has three double sockets on it. Is there a limit to the number of sockets i can have on a ring?

cheers :)
 
Sponsored Links
No, provided the total floor area does not exceed 100m2
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top