• Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.

alpha cbx combi boiler fault

Joined
1 Dec 2007
Messages
4,382
Reaction score
997
Location
Wiltshire
Country
United Kingdom
got a alpha cbx combi, both the neons are flashing (one then other) book says its pressure. pressure is fine on gauge. checking the electrics, it tells me the pcb is faulty.

any thoughts?

thankyou.

(p.s, i am corgi, just doing some weekend work on breakdowns.)
 
sludge in pressure sensor? Have you proved it?

not had to change a cbx pcb to date.

Diagnosing from flow charts in the comic's is great for a laugh as it always defaults to change pcb.
 
sludge in pressure sensor? Have you proved it?

not had to change a cbx pcb to date.

Diagnosing from flow charts in the comic's is great for a laugh as it always defaults to change pcb.

cheers, you were quite correct, i bridged the terminals, unit worked. so i cleaned old sensor, it worked but failed twice in the 30 mins i was on site. so replaced and its sorted now.

cheers, Tim
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top