Bang when central heating shuts off

Joined
20 Mar 2009
Messages
22
Reaction score
0
Location
Norwich
Country
United Kingdom
We have had a new heat only boiler installed this January. Just recently when the central heating shuts off there is a loud bang, it doesn't do it every time, but I can't figure where the noise is coming from. The pump is in the airing cupboard along with 2 motorised valves. Any ideas please?
 
Ours was a slightly different situation which took ages to solve as pretty much every other post talked about a bang when the CH shut off. Our system is a 3 port valve model with a separate 2-port safety valve for the Megaflo HWC.

We eventually worked out we had a build up in pressure at the Megaflo 2-port valve in CH only mode - HW was off. The wiring for the 2-port valve was connected to the tank thermostat. When the HWC dropped in temperature it caused the 2-port to open, triggering a pressure wave and a subsequent bang. Highly unnerving.

Eventually fixed by a local plumber who came up with an ingenious solution to connect the 2 port wiring direct to the overheat sensor on the Megaflo instead. So we are still protected but now have silence in the system! Phew.
 