baxi combi 105e HELP

Joined
11 Mar 2008
Messages
1
Reaction score
0
Location
Derby
Country
United Kingdom
Help if u can. Always had problems keeping pressure up after being fitted 18 months ago. Found 2 leaks that plumber missed. But still losing pressure every 2 weeks. Noticed though when pressure was at 1.5 bar and ch had been on a while that the pressure increased . it was going above 2 bar and rising.. I turned heating off and it seemed to stabilise. Could it be poss that it rises above 3 bar and triggers the releif valve and then drains off water, thus over time losing pressure. Have u an answer to this prob. also are leak sealers recomended for small leaks.
 
Sponsored Links
Id start by checking the expansion vessel, see faq's for step by step guide.

I would imagine that the water is being discharged by the pressure relief valve as you say. Remove and check/clean PRV when boiler is drained for repressurising.
 