• Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.

Variable combi pressure

Joined
5 Feb 2005
Messages
26
Reaction score
0
Location
Dyfed
Country
United Kingdom
boiler pressurised to 1 bar and holds it steady. Preheat DHW and pressure drops to 0.5 bar. When CH on pressure increases to a max of 2.9 bar. Bolier is Baxi 105e and recommends pressure between 1 and 1.5 bar. I would appreciate views on this problem.

Thankyou

Charlie
 
Your pressure vessel / expansion vessel needs pumping up. Lots of posts, do a search.
 
ChrisR said:
Your pressure vessel / expansion vessel needs pumping up. Lots of posts, do a search.

yes, have done so guessed the vessel needed inflating or replacing. Just hoping it might be something simple, like a faulty guage. Thanks for the response though. I'll get me kit.....
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top