Biasi Garda HE M96.28. Intermittantly no d.h.w. when c.h. is on. Indicator lamps show "no primary flow" - this is due to the pump switching off. I've witnessed the fault occuring and the sequence looks like this:
1. c.h. running
2. d.h.w. demand
3. burner shuts off
4. pump stops and does not restart*
*When c.h. is on the pump always stops momentarily on d.h.w demand but is uninterupted when changing back from d.h.w. to c.h.
I've had the PCB out and thought I'd struck gold when I found a dry joint on the pump relay but the fault is still there.
It mostly happens in the morning after c.h. has been running for an hour and just as the wife steps under the shower - you can see my problem.
Any help would be appreciated.