OK thanks for that, as suspected one of your zone valves is calling for heat, either a seized synchron motor , or a stuck micro-switch, as the heat is getting away from the boiler I suspect a seized botor, in your first pic you have two zone valves (silver boxes) these have a little manual lever on the side , turn heating and HW off and try and slide the manual lever across to the manual position, both should show resistance, if one doesnt show resistance that is your fault
Right!! Thank you so much for your help.
So the bottom silverbox, which I believe is for the HW, has resistance. The top one, does not. It's totally lose. It lights up if I turn the CH on, but you're saying that the internal motor is probably busted?
Should I replace the whole valve or is there osmething internally i can replace?
Thanks!