Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.
The number of loops is largely immaterial to the boiler.
The 'TRV' on the manifold can shut off the flow when the manifold gets up to temp, whatever the number of loops.
I'm sure an external bypass would help, but the facts remain that;
-the system boiler has an internal bypass
-it has apparently worked fine for 5 years
Therefore something has changed recently. It could be due to a number of things, perhaps the pump is not working properly, the internal BV has jammed, the flow temp NTC is defective.
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local