boulter buderus oil combi boiler

Joined
29 Jun 2007
Messages
1
Reaction score
0
Location
Nottingham
Country
United Kingdom
when our 2 year old boiler fires up it starts with a bang and the housing rattles. Has anyone else had a problem like this and what did they do please. It has done it from new, but it is very irritating. Our service engineer can come up with no cure. any help at all please.
 
Sponsored Links
Why was it not called in at the start under warranty :eek: Must be some sort of explosive ignition where the ignition is not coming in soon enough, thats what it would be with gas. I'm no oil engineer, but surely the principles are the same :confused:
 
The place to start will be the air setting which may be too high, then electrode settings, possibly nozzle also due for change. In any event the burner is either not commissioned correctly or settings need checking if not serviced annually. This may have led to premature baffle failure which would also contribute to symptom. Can almost rule out manufacturing defect.
 