Cable Runs In Loft

Invisible-Man said:
Hi,
Well I would not say that they are buried in insulation, as I have lifted all wiring (sitting on top of insulation), I was then going to board the loft with chipboard, therefore the wiring would be touching the chipboard along with the insulation.

What do you think!
:(

To qualify for Method 15, the "thermally conductive" surface must have a u-value of at least 10 W/m²K. Chipboard is only 2-3....
 
Sponsored Links
Whats plasterboard?, OOI?

first one to say "well its plastic sandwiched between paper.." gets a slap with a wet fish :LOL:
 
Could you supply me with a link to method 15 etc, also I am trying to find where the appendix 4 charts/diagrams are

Many thanks :(
 
Adam_151 said:
Whats plasterboard?, OOI?

first one to say "well its plastic sandwiched between paper.." gets a slap with a wet fish :LOL:
Why would anyone say that? It's plaster sandwiched between paper ;)

9.5mm baseboard is about 16.
 
Sponsored Links
Hi,
So touching 9.5mm plasterboard one side and touching insulation the other side of a wiring route is acceptable!

Also a link to the method 15 etc and appendix 4 diagrams would be useful

Many thanks
 
Invisible-Man said:
Could you supply me with a link to method 15 etc,
Wr250.jpg
http://www.iee.org/Publish/Books/WireAssoc/index.cfm?book=WR 250

also I am trying to find where the appendix 4 charts/diagrams are
Wr250.jpg
http://www.iee.org/Publish/Books/WireAssoc/index.cfm?book=WR 250
 
That's not the Wiring Regulations.

It's not even a guide to the Wiring Regulations.

It's a guide to one part of the Building Regulations.

The book shown above with the brown cover is the Wiring Regulations.
 
ban-all-sheds said:
Why would anyone say that? It's plaster sandwiched between paper ;)

:oops: Sometimes I really do think my hands ignore what my brain tells them to type in lieu of something that sounds some-what similar :LOL:
 
ban-all-sheds said:
That's not the Wiring Regulations.

It's not even a guide to the Wiring Regulations.

It's a guide to one part of the Building Regulations.

The book shown above with the brown cover is the Wiring Regulations.

Thanks for that, would you say that for a solution, a 1" air gap would be sufficient? Also would wrapping or laying wires in or on silver foil would help to disperse heat generated? :rolleyes:
 