On my open vented y plan central heating system the cold feed pipe that goes up into the F&E tank gets really hot. The expansion pipe (larger 22mm diameter one) doesn't.
You have two pipes.
One is Feed and Expansion, the other is VENT.
Expansion water goes into the water tank the same way it came out. The vent is a column of water which only goes up and down an inch or so.
It/they both get hot through convection, unless you take steps to prevent it.
They both have a level change when the pump stops & starts, quite a kick if there's any air in the system at all. You will have some air for a few days after a PF. Bubbles inthe water.
So you can insulate if you like, but otherwise don't worry unless there's air being sucked into the vent (try holding a cup of water to it) or water coming out of the vent.
Yesterday after the power flush there was water coming out of the vent when the pump stopped. We only discovered this as the vent wasn't quite over the F&E tank so ended up on the loft floor.
Hopefully that is just because there is still air in the system and it will soon settle down.
Yep, pretty normal, for a few days sometimes. The trapped air acts like a spring so when the pump stops and it's no longer compressed it pushes back.
If it won't quite stop, you could take the loop (inverted U) of the vent pipe a bit higher. You don't want it circulating, because that takes oxygenated water fom the tank down into the system, which eventually leads to needing another powerflush ..
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local