What is the required fall of condensate pipework if ran in 1.5inch pipe? Is it 44mm per meter?
 
Is that just for 22mm condensate pipework then?
 

Attachments

  • Screenshot_20210312_213813_com.google.android.googlequicksearchbox.jpg
    Screenshot_20210312_213813_com.google.android.googlequicksearchbox.jpg
    311 KB · Views: 78
Yup, the optimum for any waste pipe is 45mm. The regs ask for a min of 20mm to a max of 90mm, in the middle is the best IMO or as suggested, the manufacturers requirements.
 
Yup, the optimum for any waste pipe is 45mm. The regs ask for a min of 20mm to a max of 90mm, in the middle is the best IMO or as suggested, the manufacturers requirements.

Middle would be 55mm </pedantry> ;-)
 
Steeper fall might be better to prevent icing and it's not carrying solids.
 