Hi all, I'm a newbee so sorry if topic already covered but lots of different info so just to say my scenario
Just moved into a new house with a Oven wall connection plate with 45A DP wall switch higher up (no additional socket).
The radial cable if fed straight from the 'old type' 32A hard wired fuse consumer unit. The wire looks to me like it is 10mm grey T&E but I need to confirm it is not 6mm as its a possibility?
My new Hob has a max rating of 6.5Kw and the single oven is 2.5Kw so a potential unlikely max of 9Kw similar to a shower I guess.
The Hob instructions say to use 2.5mm cable less than 2M long but no size quoted for the Oven?
The wall plate has a hole at the bottom but it looks tight to wire both cables into so I have two thoughts:
1) As both appliances have terminal connections on the back, wire the Oven to the hob first then wire the Hob to the wall plate. If so do I need to beef this up from 2.5 to say 4mm?
2) Use a heavy duty junction box like used for tails?
If the potential max current is 37.5A (9000W/240v) then I assume the 32A fuse would be about right as can't they handle a lot more and better for it to blow that a fuse too big?
This must happen a lot so what do most people do? Any experts willing to point me in the right direction greatly appreciated!! Cheers
Just moved into a new house with a Oven wall connection plate with 45A DP wall switch higher up (no additional socket).
The radial cable if fed straight from the 'old type' 32A hard wired fuse consumer unit. The wire looks to me like it is 10mm grey T&E but I need to confirm it is not 6mm as its a possibility?
My new Hob has a max rating of 6.5Kw and the single oven is 2.5Kw so a potential unlikely max of 9Kw similar to a shower I guess.
The Hob instructions say to use 2.5mm cable less than 2M long but no size quoted for the Oven?
The wall plate has a hole at the bottom but it looks tight to wire both cables into so I have two thoughts:
1) As both appliances have terminal connections on the back, wire the Oven to the hob first then wire the Hob to the wall plate. If so do I need to beef this up from 2.5 to say 4mm?
2) Use a heavy duty junction box like used for tails?
If the potential max current is 37.5A (9000W/240v) then I assume the 32A fuse would be about right as can't they handle a lot more and better for it to blow that a fuse too big?
This must happen a lot so what do most people do? Any experts willing to point me in the right direction greatly appreciated!! Cheers