I've suggested this might be the case, and I think these readings confirm it. Does anyone agree, and agree with what I might do to fix the heat loss?
Open vent system, cylinder mounted in the first floor airing cupboard, Vaillant 418 boiler, downstairs, high on kitchen wall, some 12 feet away, horizontally. MOMO type, 3-port valve, which remains parked, in the last configuration used - in this case, open to HW cylinder. All the main pipe work, is 22mm
I have this week added an ebus adaptor, and Rpi, to download, and decode the data, which produced this, some four hours after the boiler last needed to fire....
harry@Rpi5:~ $ ebusctl read -v flowtemp
bai FlowTemp temp=35.12;sensor=ok
harry@Rpi5:~ $ ebusctl read -v returntemp
bai ReturnTemp temp=40.12;tempmirror=64893;sensor=ok
The cylinder was heated to 65C, but without any water being used, it was gradually still dropping, quicker than I would expect.
Those readings, suggest to me, that heat is being lost from the cylinder, back to the cylinder coil, along the return pipe, to the boiler, where it is cooled, then along the flow pipe, via the 3-port.
So I am again looking at ways to stop the thermo syphon, maybe a 22mm anti gravity valve, and where I could manage to squeeze one in. It cannot be in the return close to the boiler, the mag filter is squeezed in there. Can these things be mounted horizontally, in the long horizontal return run, or would it work in the flow, equally well?
Open vent system, cylinder mounted in the first floor airing cupboard, Vaillant 418 boiler, downstairs, high on kitchen wall, some 12 feet away, horizontally. MOMO type, 3-port valve, which remains parked, in the last configuration used - in this case, open to HW cylinder. All the main pipe work, is 22mm
I have this week added an ebus adaptor, and Rpi, to download, and decode the data, which produced this, some four hours after the boiler last needed to fire....
harry@Rpi5:~ $ ebusctl read -v flowtemp
bai FlowTemp temp=35.12;sensor=ok
harry@Rpi5:~ $ ebusctl read -v returntemp
bai ReturnTemp temp=40.12;tempmirror=64893;sensor=ok
The cylinder was heated to 65C, but without any water being used, it was gradually still dropping, quicker than I would expect.
Those readings, suggest to me, that heat is being lost from the cylinder, back to the cylinder coil, along the return pipe, to the boiler, where it is cooled, then along the flow pipe, via the 3-port.
So I am again looking at ways to stop the thermo syphon, maybe a 22mm anti gravity valve, and where I could manage to squeeze one in. It cannot be in the return close to the boiler, the mag filter is squeezed in there. Can these things be mounted horizontally, in the long horizontal return run, or would it work in the flow, equally well?