can anyone tell me, can a 4.4kw d/oven with a 3.8kw seperate hob be run of 1 circuit with 32amp fuse at consumer unit with 6mm twin earth.
and can you have 1@ cooker control (45amp) or would seperate control be required for each appliance
 
Sponsored Links
At full blast the load of the two combined is about 35amps.

But you'll never have them on all rings and both ovens at full blast. There's a technique called "Diversity" that allows the designer to "over budget" the circuit for some devices.

So you'll be fine.

One isolator is OK too.

You biggest logistical thing will be terminating two 6mm² cables. The terminations on the oven and/or the hob won't be good enough for that. I suggest you use one of these:

Made for the job PRW217
 