Out of interest, what make was the MCB?
Put your hand down, that boy.
A wonderful example of the importance of correct punctuation.Put your hand down, that boy.
A wonderful example of the importance of correct punctuation.Put your hand down, that boy.
Out of interest, what make was the MCB?
Wylex (NHX B20)
When one is dealing with very high currents and very short disconnection times, I suspect that this is not really quite as much a ‘science’ as we might like to think – which is perhaps the reason for some of the ‘unexpected’ behaviour one sees in these various ‘discrimination (or non-discrimination) stories’.I can't seem to find a curve for the 5A BS 1362 fuse, but it looks probable that the fault current was in excess of what was needed to blow the fuse within 0.01s seconds. From what I can deduce by Wylex's literature, their MCBs, in common with many others, take minimum that long to trip anyway, so the fuse was always likely to blow. Whether a BS 1361 or 88-3 (whatever they are now) would have avoided this, I could not say, but as they are not limited by a physical mechanism, it is likely.
He said that there wasn't even a bang - just 'silence' as the trimmer stopped. I suppose there is really 'no telling' exactly what is going to happen when one chops through a cable in this sort of way. There is certainly the possibility that the duration of the L-N contact could be extremely short - too brief for any OPD to operate. It is even just about possible that it could happen without there ever being any electrical connection between L and N - one conductor could be sliced and 'pushed out of the way' before the other conductor came into contact with a blade. ... and, of course, if it were all over incredibly quickly (say <1 ms), whilst the supply waveform happened to be around its zero-crossing point, there might not actually be much of a fault current.Yes John, an exact replica of my neighbour's sliced mower lead - just a big bang but nothing tripped.
And for a type D they're downright confusing.Finding adequate information (‘curves’) for the operational characteristics of OPDs is not easy. The curves in BS7671, for both fuses and MCBs, ‘stop’ (i.e. don’t go below) at 100 ms.
I've often wondered why this is the case - I can see how it's technically correct, but it takes some getting used to.Even this is a bit misleading – to reflect reality, there really ought to be a gap in the curve between 5 seconds and a very much lower current (maybe ~10ms), since the implication of the curve that magnetic operation can take anything up to 5 seconds clearly is not correct.
Which is the achilles heal of the MCB - it looks great on paper where all fault start at 0A on the sinusoidal waveform, but as soon as you have a fault occurring anywhere else on the curve, you're going to see a large let-through current before the MCB will trip. And, in the time it's taken to unlatch itself and start breaking, the downstream fuse will have removed the fault.Indeed, one wouldn’t really expect operation time for an MCB to be appreciably influenced by current magnitude – once a current equal to or above the ‘threshold’ is reached, the actually tripping is yes/no, after which the operation time is just down to how fast the mechanical mechanism operates.
That is a typical time from BS EN 60898, however the let-through energy graph from the same literature says "HW=0.01s". I've assumed this is the time they've used to calculate what else is on the graphs, but I can't find where HW comes from.The Wylex MCB data I’ve seen is also a little misleading in another respect, because they show the ‘vertical’ magnetic part of the curves right down to 1 ms, and I don’t believe that they ever operate that rapidly. The text of the Wylex technical documentation indicates that their standard MCBs generally operate in 3.5 to 5.0 ms.
I would not say that it is even technically correct. By presenting it as a continuous curve, it implies that it is possible to get operation times between (for the BS7671 curves) between 100 ms and 5 seconds with a current at the minimum level which should result in magnetic tripping (e.g. 5*In for a Type B MCB), and I don’t think that’s correct or possible. The Wylex curves are even more incorrect, in that the continuous curve implies that it’s possible to get any operation time between 1 ms and 5 seconds at that current. As I said, there should be a gap in the curve between 5 seconds and the longest possible operation time at that current (say, about 10 ms).I've often wondered why this is the case - I can see how it's technically correct, but it takes some getting used to.Even this is a bit misleading – to reflect reality, there really ought to be a gap in the curve between 5 seconds and a very much lower current (maybe ~10ms), since the implication of the curve that magnetic operation can take anything up to 5 seconds clearly is not correct.
Given that we seem to be talking about operation times which will usually be less than half a cycle (possibly, per Wylex, no more than quarter of a cycle), I don’t even know at what current they are meant to ‘trip’ (‘unlatch’). When we say that, for example, a B20 should result in the magnetic trip at “100A” what does this actually mean? The calculations (e.g. of PFC etc.) we do are in terms of RMS voltage and current. So, do we expect the B20 to trip at an instantaneous current of 100A ('RMS') or the corresponding peak current of about 141A, or what?Which is the achilles heal of the MCB - it looks great on paper where all fault start at 0A on the sinusoidal waveform, but as soon as you have a fault occurring anywhere else on the curve, you're going to see a large let-through current before the MCB will trip. And, in the time it's taken to unlatch itself and start breaking, the downstream fuse will have removed the fault.