    Hi,

    I have a problem with my Combi boiler whereby the pressure rises to about 3 bar when the central heating has warmed up but if I switch off, the pressure drops to Zero!!! If I leave the heating on it works perfectly although the pressure is high obviously. When the pressure drops I have to refill using the filling loop. I top up to just over 1 bar but again, when the heating kicks in and warms up it rises to 3 bar. Any help would be greatly appreciated.

    Cheers ;)
     
  2. hect

    hect

    Joined:
    9 Jan 2009
    Messages:
    168
    Thanks Received:
    0
    Location:
    Humberside
    Country:
    United Kingdom
    Possibly exp vessel - is your PRV passing?
     
  3. jackthom

    jackthom

    Joined:
    14 Feb 2007
    Messages:
    1,283
    Thanks Received:
    227
    Location:
    Northumberland
    Country:
    United Kingdom
  4. johnnywishbone1

    johnnywishbone1

    Joined:
    11 Jan 2009
    Messages:
    12
    Thanks Received:
    1
    Location:
    Mid Glamorgan
    Country:
    United Kingdom
    Thanks gents, I'll give it a go this weekend ;)
     
  5. Sponsored Links
  6. johnnywishbone1

    johnnywishbone1

    Joined:
    11 Jan 2009
    Messages:
    12
    Thanks Received:
    1
    Location:
    Mid Glamorgan
    Country:
    United Kingdom
    Right then, so I have just changed the expansion vessel after draining down the system as per the FAQ instructions. I didn't actually have any water coming out of the schrader valve of the original which would indicate a defect but I decided to change the tank anyway as I already had the spare one ready to go. It was £42 from plumb centre so not the end of the world. After refilling the system and bleeding all the rads I noticed something strange. On the bottom cover I saw dry green gunk !!! When I looked above it I could see it had been coming from the automatic air vent attached to the air seperator. It's a knurled thumb screw which is quite difficult to get at. Firstly I tightened it down but then no air could escape when the central heating was running and so I opened a little and could hear air escaping and could see air bubbling through the green stuff for about 30 seconds and then stop. I assume this is to relieve the system of trapped air ? Any ideas anyone ?? ;)

    Also, any ideas how best to replace the inhibitor in the central heating ?

    Cheers.
     
  7. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page