few questions
14 Sep 2004
how do you get the Ze @ origin? and is the short circuit capacity the Ze X voltage?
also, what is R1, R2 and Zs?
The term Ze specifically means the earth fault loop impedance at the origin of the installation, so no need for the "@ origin".
For that you would simply use a Earth-fault loop impedance tester.
Do you mean "prospective short-circuit current"? If you do, then it isn't. No relation at all. You need a prospective short-circuit tester.
R1 and R2 are used for testing ring circuits.
Zs is the earth-fault loop imediance at an accessory.
R1 & R2 are the resistances of the phase and protective conductors respectively.
Therefore Zs = Ze + R1 + R2.