Fuse spur switch won't turn on after replacing Honeywell ST9400C
11 Oct 2026
It was a like-for-like replacement (with a new ST400C) where the old one was taken off the back plate and the new one slotted in (without touching any of the wiring), but just as the new one slotted into place, the fuse indicator light on spur went off and the boiler switch in the fuse box tripped. I have since changed the fuse in the fuse spur socket twice with new 3A fuse (same as before), but it won't switch on. The wiring in the backplate is in tact. The wiring in the fuse spur socket is also in tact.
Any ideas what could be the problem.
If you are changing one ST9400 for another then from your description it must be faulty as you appear to be putting a short across live and neutral or earth. Are you sure the old one wasn't a slghtly different model that requires wiring to different terminals as shown in the instalation instructions
Replacement Wiring
If using the ST9400 to replace other Honeywell Programmers, the equivalent wiring terminations are shown in the tables below.
ST6200/ST6300/ST6400 L N 1 2 3 4
ST9400 L N 1 2 3 4
ST699/ST799 L N 3 4 5 6 7 8
ST9400 L N 4 2 not connected 3 1 not connected
ST7100 L N 3 4 5 6 7 8
ST9400 L N not connected 2 4 not connected 1 3
ST7000A L - 2 3 4
ST9400 (see notes 1, 2) L N 1 3 4
Notes: (1) A permanent mains supply must be provided for the ST9400 Programmer.
(2) ST9400 must be confi gured as a Mini-Programmer
Here are the pics of the old and the new. The first programmer is the old one, the other is the new (well new in the sense it was bought in the last few days but not brand new).Third pic is wiring as it is with existing programmer. The wiring hasn't been touched. Reason for replacement is the text on the old one is extremely faded and the buttons require a lot of effort to turn on and off and switch between different options on the programmer.
Just below the backplate there is a relay box (Honeywell) and right of it the fuse spar switch
You say the wiring hasn’t been touched, yet on your wiring picture:
There is no neutral wire in the N
You have a CH off (blue - I suspect this is the N) and this screw looks more prominent than others
I had the two programmers switched by a builder (he also works with electrics when he needs to). I am sure he didn’t touch or switch any of the wiring around. I was away for a while when he was replacing them. I can’t be 100% sure simply because I wasn’t there when he did it and I hadn’t taken a picture of the wiring before he replaced the programmers.
Finally, a bit of sense. As I said, you have no neutral and a CH off. Inform the builder he has done it wrong. If it was swapped on the backplate, the replacement would work unless faulty.
  • Thanks
Reactions: DP