I'm looking to add some additional sockets in garage shown in black pen. Am i able to connects these to 32mcb socket using 4mm cable on a radial? Does the 2.5mm radial already there look OK?

Thanks
 

Attachments

  • 20230131_125901.jpg
    20230131_125901.jpg
    116.3 KB · Views: 79
Sponsored Links
I'm looking to add some additional sockets in garage shown in black pen.
Can't really tell the difference.

Am i able to connects these to 32mcb socket using 4mm cable on a radial?
Yes - assuming the cable is clipped to wall or buried in masonry.

Does the 2.5mm radial already there look OK?
Yes - with the same proviso.

You don't need the 13A switch (Fused Connector Unit ?) when there is a 20A MCB.
 
Thanks. Yer the 13a switch was already there with the 20a mcb.
 