morning all, i've a shed 60m from the house and i'm wanting to put a couple of lights and sockets in there. i'm guessing an exstension lead wouldn't cover my needs, what would?
 
A bloody good reel of 2.5mm S.W.A and a qualified electrician :)
That qualified electrician might not be too impressed with the 2.5mm² SWA, unless the design load is very low. At 60m, buried 2.5mm² SWA would hit the limit for acceptable voltage drop for the lighting at a total load of about 6.4A.

Kind Regards, John.
 