Twin and earth through an under ground duct to a garden shed, no RCD protection.
Cable insulation is not good and duct flooded. Electrolysis of the water has created hydrogen and oxygen which came out of the duct into the shed.
Gas from the duct collected in a polythene bag over several hours did burn extremely rapidly when ignited confirming the gases were from the electrolysis of water.
Only small volumes of gas being produced and a well ventilated shed meant the hazard of explosion was virtually nil.
Cable disconnected and IR tests showed failure of insulation. Cable resisted all attempts to drag it out of the duct. Markings on cable show the cable at one end is not the same as the cable at the other end. There has to be a joint of some type in the duct.
A previous owner of the property was an avid DIYer.