Grant CHP no light

Joined
22 Oct 2023
Messages
2
Reaction score
0
Country
Ireland
Grant combi boiler. No light on CHP but programmer set to constant, no electrical power to pump, DHW light on and pump running but programmer set to off. Checked one way value on CHP and free and working. Changed programmer but fault remains, System has been operating for several years without any problems.
 
Which model Grant combi there are several
Is dhw working normally? DHW pump running suggests a demand .
Do you have a multimeter and are competent to use it?
 
The boiler is Grant Vortex External Combi 36kw.
I can use a multi meter, I have checked the supply to the CHP and there is not power.
 
If DHW pump is running heating just won't work,
DHW needs to be satisfied for ch to work.
Check if there is a feed back from flow switch they can stick open.
Also check all air valves if there is any air at all in boiler and pipework the DHW pump can run but not actually properly circulate the heat store.
 