Good morning experts!
My Grundfos pump is running constantly. I have it on the first setting, so it runs quietly, but I can hear it pumping water. I haven't used my boiler for months since it's obviously been summer. I thought the pump was on tickover and was meant to stay on 24/7.... until I seen my electric bill I thought i'd query it!
I noticed a problem over winter where if I put the hot water on only, the radiators will also get red hot - even though the heating setting was off on the boiler controller down stairs.
I have noticed the 3 port valve header/cover/housing gets really hot and the lever is floppy (I can move the lever, but it doesn't seem to have any friction - i.e swings loosely). Could the 3 port be the problem? I am unsure why the pump would always be on.. AND why my heating comes on when I just want hot water.
Thanks in advance for any replies
My Grundfos pump is running constantly. I have it on the first setting, so it runs quietly, but I can hear it pumping water. I haven't used my boiler for months since it's obviously been summer. I thought the pump was on tickover and was meant to stay on 24/7.... until I seen my electric bill I thought i'd query it!
I noticed a problem over winter where if I put the hot water on only, the radiators will also get red hot - even though the heating setting was off on the boiler controller down stairs.
I have noticed the 3 port valve header/cover/housing gets really hot and the lever is floppy (I can move the lever, but it doesn't seem to have any friction - i.e swings loosely). Could the 3 port be the problem? I am unsure why the pump would always be on.. AND why my heating comes on when I just want hot water.