help please with worcester 24i

Joined
24 Dec 2007
Messages
3
Reaction score
0
Location
Essex
Country
United Kingdom
Hi wondering if you can help at all?

I have put on a new automatic purger and a primary overflow, on my worseter 24i combi boiler (not the junior, its the standard one.) as it was leaking through the automatic purger and the overflow had a crack.

when i put the central heating on the pressure rises till i turned it off.

pressure outlet activated at 1.8 bar. (for the water)

is there something else i should be doing? any help would be appreciated
 
Sponsored Links
Check the expansion vessel pressure.

See FAQs on how to this and re-pressurise it.
 
Sponsored Links
many thanks i think i have it sorted ..repressurising it has done the trick

many many thanks and a merry xmas

Diane
 
its your expansion vessel stick a screw driver in the valve if waters comes out take the boiler of the wall and change it alternativly it might just need pumping up

also check the pressure relief valve and open the prv when you pump up the vessel
 