Help tenant heating issues!

Joined
7 Aug 2016
Messages
6
Reaction score
0
Country
United Kingdom
I live in a Victorian end terrace. I'm hardly in and get home from work at 6pm everyday.

The house is ice cold. I usually go straight upstairs to my bedroom with the thermostat and set it to 20 degrees. Its taking nearly 2hrs for the room to even get to 17 degrees.
The radiator does get pretty hot all over, it a long one across under the window. I can only touch it for about 10 seconds, downstairs radiators are all on too and also get hot and are warming downstairs ok but bedroom taking ages.

The boiler is pretty new, pressure is at 1.2psi. Not turned up to max radiator temp yet but not far off.

What can I do?

Does my landlord need to get a plumber in to fix it? He keeps telling me to turn the downstairs radiators down?

Many thanks for your replies!
 
Last edited:
As above, if the rads are heating up but the room isn’t, then I would say room/heat loss issue, or rad too small. Unless it’s heating too quickly.
 
It sounds like you might be losing heat out of the window...

A couple of easy fixes:
- Make sure there's a thick curtain between the radiator and the window, with no gap at the bottom
-If the window doesn't have secondary glazing, then use the cling film and hairdryer type

-Check for draughts
Check the depth of the loft insulation
 
Word bedroom is the first clue

Design temperature for the bedroom is 16. It is reaching 17 degrees punching above expectations but will never reach 20 unless heat loss is calculated for 20 not bedroom 16.

I suspect the bedroom radiator is achieving the target despite boiler stat not being at max so additional factor of 10% is hence raising the room temperature to 17

Finally.
When you wrap your hands around the radiator valves, are both the valves red hot, very different temperature wise, little difference, slightly greater difference? Placing hand on top of radiator is no indicator of radiator performance. If a radiator needs 100 gallons of water an hour for rated heat output, yet it is supplied twice that amount or fraction thereof, top of radiator will feel the same
 
I have when I still went out every day, set a sequence of heating before my return. Not much of a delay between each radiator calling for heat, only 5 minutes or so, but it did work, also found with some thermostatic radiator valves (TRV) the anti-hysteresis software was OTT, so would set 2°C higher for the first hour, but main reason for not being to temperature on time, was a darn wall thermostat turning off the whole boiler.

With the likes of Drayton Wiser, every room can have its own control, but unless that's the case, it is all too easy for the boiler to turn off too early. You say thermostat set to 20°C I assume that is in the bedroom?

I had a cold living room, I also thought the radiators were working OK, always seemed warm to the touch, but the hall thermostat was simply turning off too early, once a boiler linked thermostat was put in the living room, it worked fine.

In the main as said bedroom are kept cooler, when a house is made into a bed sits, then clearly the heating has to change, giving all units the option to run boiler and get the room warm.

If the radiator is hot, all over then it should heat the room, what I found was a 2 kW oil filled radiator which was less than a 1/3 of the size of the water radiators was heating the room fine, so it was clear the central heating radiators were turning off.

I did find insulation behind radiators helped, so heating room not the outside wall, and shorter curtains, and a bit of Sky board, the stuff used to make signs, on the window sill, so the heat was directed into the room rather than to the trickle vents on the top of the window, made a huge difference, also closing the trickle vents.

The orignal long curtains were directing the heat to the window first, I see the idea of a radiator under the window, it is a place where we don't want to put other furniture, but for heating the room it's a daft location, one the heat goes out of the window, and two it is against a cold wall, so the TRV heads turn on prematurely, but not really easy to move, so all we can do is put a sensor/thermostat on the opposing internal wall, linked to the TRV, so it's not affected by wall temperature.

But as said bedrooms are normally set to 16°C not 20°C so maybe radiator simply not big enough, not sure how well these
1795520517981.png
work, I tried a standard upright fan and it was too much, all it did was cool the radiator down, but a small one, which directs heat into the room may help, as will spraying the radiator mat black.

I remember a collage science department doing that, the lecturer felt he could not keep telling people mat black was the colour to use, and have all the radiators shiny white, it worked too well, science department was toasty warm, but it had cooled the water down so much, rest of collage was cold, so next year it returned to shiny white.

But look at any radiator which is covered, and it is mat black, be it in a car, or a fan assisted radiator, radiators should be mat black.
 