immersion heater

Joined
26 Oct 2008
Messages
2
Reaction score
0
Location
London
Country
United Kingdom
if i test across the l - n on immersion sholud i be getting about 20ohms and 0.00 resistance or is it knackered?
 
With the supply isolated and the meter on resistance you should have a reading of around 20 ohms.
IR readings should be above 1 megohm between the element and earth.
 
About 20 Ohms with the thermostat contacts closed is good.
Approaching infinity if the 'stat contacts are open.

You may be able to see the change from about 20 ohms to out of range (or whatever your particular meter displays) as the 'stat switches if you change the temperature setting.

Some thermostats incorporate an overheat cut-off that may require re-setting. It should trip if the thermostat doesn't operate correctly.
 
:D i've got 20ohms continuity and 0.00 megohms insulation resistance between live and neautral so element should be ok still, wicked
 
You aren't measuring insulation resistance unless it's between either L or N, and Earth. Actually, I'm not sure what you're really doing anyway. Presumably there's some sort of problem?
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top