issue with baxi 105e combi

Joined
24 Jun 2008
Messages
14
Reaction score
1
Location
Gloucestershire
Country
United Kingdom
hello, this is my first post here so any help would be appriciated. Have just changed the diaphram on my baxi 105e but i still have a issue. when the hot water has been used and the tap is switched off, after about 2 minutes the boiler will click into 'humming mode' then fire up c/h (even if selector switch is on hot water only) for about 1-2 mins. It will then click back to humming mode and then eventually back off. did have the 'radiator with a strike though' warning light on a couple of weeks back but nothing since. could it be a temp sensor??? - again, thanks for any assistance.
 
Sponsored Links
Whatever else is happening, it would be wise to change the primary thermistor to eliminate any problem with it.

Relatively cheap, Prt No. 5108265 dry pocket and 'low voltage'.
 