Main Protective Bonding query.
20 Apr 2009
Hi there. I found this forum through Googling for an answer to a question I have regarding main protective bonding. I have read so many 'answers' but am not really any closer to an knowing what I should do. Perhaps one of you experts on here can help me out.
I am currently refitting my kitchen. This doesn't involve changing any electrics other than straight replacement of socket outlets and so I didn't envisage any problems in this area. However on taking out the sink units I find that there is no earth bond cable on the incoming water supply. Now from what I have read, the incoming water supply pipe should be connected by a cable from within 600mm of the stopcock to the Main Earth Terminal back at the consumer unit and should be less than a certain resistance, (I can't remember the exact figure I saw mentioned but it was quite low, a fraction of an ohm). In my case the stopcock and the incoming electricity supply are opposite sides of the house. The Gas supply enters the house right next to the electricity supply and there is a earth wire between the MET and the Gas pipe coming off the gas meter so ok there I guess, but to reach the cold water supply the earth wire would have to be of a ridiculous length such that the resistance of it would surely reduce it's effectiveness anyway in the event of a fault, especially by the time it was routed neatly across the house, which would be quite a task in itself. Now perhaps I have totally mis-understood it all and so would be grateful for any advice or clarification anyone could give me.
I might add that I am an electronics engineer by trade and so understand the principles involved in electrics, although having said that, getting my head around the regulations as to what the unqualified homeowner can and cannot do himself I find a nightmare. How do you guys manage to keep up with all the seemingly ever changing regs?
While on the subject of the regs could I be cheeky enough to ask another question in the same post? Could I legally extend the existing 45amp radial cooker connection myself in order to re-position the cooker? I know I'm not allowed to install a whole new cooker circuit but this would just be extending an existing one.
Thanks in advance for any help or advice you might give me.
Donald.
Firstly your water bond would usually be 10mm based on a 16mm main earth from your cutout to the fuse board with 25mm live and neutral. The resistance should be less than or equal to 0.05ohms which would give you a maximum run (in theory) of around 30m. However, in reality you can go a fair bit further then 30m and still meet the readings as most calculations are based on worst case scenarios rather then real world ones.
Regarding the extending the cooker cable, if it's making up part of the fixed installation and with it being in a kitchen it becomes notifiable work. That means that you shouldn't be doing it unless you are competent, able to test and you get the Local Building Authority in to sign it off for you. Usually it's easier to get an approved electrical contractor in who shouldn't charge you too much as long as the existing installation is sound.
Thank's for the informative reply ElectricDunc,
Regarding the water bond: whilst I can see the 'makes good sense' aspect of it, am I correct in assuming that (as I am just changing the sink and not modifying either the plumbing or electrics) it isn't actually a legal requirement, as it has obviously never had any bonding since the house was built (around 1970)? Is it something I would be permitted to do myself? I read elsewhere that it is not 'notifiable'. Is this correct?
Finally, just out of interest, what method would normally be used to check the resistance of the bond? (In the electronics industry we usually check earth connections by passing 25A through for X number of seconds, and measuring the voltage drop to calculate the resistance.)
As regards the new cooker I reckon I'll just stick with gas as the gas point is already in the right place!
Thanks again
Don