So I've had a silly PM asking why the bucket didn't blow a fuse, complete with a statement of poor circuit design? Even I won't admit w ho.
To explain the power installation in older exchanges and that one in particular:
There was a 50V open topped lead acid battery, each cell being appoximately 4x4x2.5ft HxWxL the full battery being ~60ft long that size battery will be circa 5000AH and at the 50V end will be a fuse of maybe 1000A (usually something up to ¼ of the AH capacity)
There was a second similar battery.
There was a suite of 'rectifiers' usually rated at 1000A with a matching fuse on the output and in a quantity to give at least 150% of peak current at the busy period and they automatically switch in as required.
In normal use both batteries and sufficient rectifiers would be connected directly to the bussbars which meander around the exchange.
That exchange had 4 rectifiers and at that time of day would have likely had 2 rectifiers running, one supplying the full 1000A and the other supplying close to a second 1000A.
Tha bussbars leading away from the battery/rectifier combination being a lamination of 6 12"x1" copper (45000mm²)
More usually each battery is arranged in 2 halves side by side but this example shows the pair in a straight line each side of the battery room, all dependant on the space available. I've known them to be distributed between different rooms and even floors.
So feeding the short circuit created by a bucket touching the bussbars are 2x1000A rectifiers and 2 batteries capable of maybe 200,000A, albeit limited by a pair of 1000A BS88 fuses. The touch of the poor bucket didn't stand a chance, it would have instantly blown a hole and as the bucket dropped down each new contact being another flash.
The installation I've tried to describe no longer exists in standard UK exchanges.