- Joined
- 15 Jan 2008
- Messages
- 191
- Reaction score
- 13
- Country
Went to a job today to install an extra socket. System is TT and I've not worked on these before so just wanted to check my assumptions.
A quick Zs at an existing socket before starting work gave me 284 ohms, carrying on testing (using method 2 for earth electrode testing) it seems as if the rod isn't doing anything and the 284 ohms was through the gas and water bonding.
No RCD up front although I think there used to be one as and old Seeboard notice to that effect was still near the head. New split load Wylex installed 3 years ago with some circuits covered by 30ma RCD but cooker and other kitchen circuits left on and old 3036 board.
Continuity of main earthing conductor from board to electrode was jumping all over the place around the 2 ohm region but connections tight unless there is a joint somewhere.
Advised that electrode and main earthing conductor need further testing/renewing and that either a 100ma S type RCD up front or new dual 30ma RCD board installed to incorporate all circuits.
Have i got it right?!
Sorry for long post..........