Whats the worst that can happen/the danger potential with this type of fault. ? Obviously on an RCD this would trip, but not on a non- rcd circuit - as I'm sure there are plenty of unkown faults of this type supplin gsockets and the like quite "happily"...
With a N to E fault on a TN-S, depending on the impedance of this fault, and how close to the origin, a percentage of the total current will flow down the N to E fault.
If this current is substantial and the earth path is not up to much, there is a huge risk of fire.
I have seen a site with over 200 amps flowing in the earth, through galv trunking, 50mm earths etc. Some fool had mixed up the N and E bar in a TP distribution board.