    Dear Forum

    I have a question re. sizing of new gas pipe to feed new Baxi Neta-Tec 33 HE combi boiler. BG provided a quote this week (I nearly fell off my chair) which included an upgrade from 15mm to 22mm pipe. I am concerned whether 22mm will be large enough as the pipe run has many twists and turns.

    I have therefore measured the run and would appreciate it if a gas guru could advise whether 28mm (or larger) is required as I not technicaly minded when it comes to calculations! Thanks.

    90deg elbow (glanded to top of gas meter)
    5cm
    90deg elbow
    20cm
    90deg elbow
    100cm
    T-piece (enable connection to 4-burner gas hob)
    87cm
    90deg elbow (to avoid supporting wall)
    30cm
    90deg elbow (to avoid supporting wall)
    28cm
    90deg elbow (to avoid supporting wall)
    30cm
    90deg elbow (to avoid supporting wall)
    185cm
    90deg eblow
    200cm
    45deg elbow
    180cm
    45deg elbow
    70cm
    90deg elbow
    0.3m
    90deg elbow (pipework now in line with boiler connection)

    Total length of pipe run is 8.5m to 9m.
    1off T-connection piece
    10off 90deg elbows
    2off 45deg elbows

    BG included the extra 22mm copper in the quote but the quote doesn't show any evidence of number of elbows. This could be because it is irrelevant or that it was not properly considered.

    Thanks in advance guys and girls!
     
  2. Sponsored Links
  3. ServiceNumpty

    ServiceNumpty

    Joined:
    9 Sep 2007
    Messages:
    6,962
    Thanks Received:
    1,697
    Location:
    Nottinghamshire
    Country:
    United Kingdom
    Who else have you had out to quote and what were their recommendations. As you only mentioned BG.
     
  4. powerbooksub

    powerbooksub

    Joined:
    3 Jul 2011
    Messages:
    49
    Thanks Received:
    0
    Location:
    Surrey
    Country:
    United Kingdom
    Hi

    I haven't had anyone else round yet.

    Do you think the 22mm sounds ok or should it be 28mm?

    Thanks!
     
  5. muggles

    muggles

    Joined:
    28 Oct 2005
    Messages:
    13,342
    Thanks Received:
    3,077
    Location:
    Daventry
    Country:
    United Kingdom
    You've failed to mention the power of your gas hob...
     
  6. Sponsored Links
  7. ianblue

    ianblue

    Joined:
    6 Feb 2008
    Messages:
    137
    Thanks Received:
    10
    Location:
    Yorkshire
    Country:
    United Kingdom
    22mm is fine.
     
  8. powerbooksub

    powerbooksub

    Joined:
    3 Jul 2011
    Messages:
    49
    Thanks Received:
    0
    Location:
    Surrey
    Country:
    United Kingdom
  9. powerbooksub

    powerbooksub

    Joined:
    3 Jul 2011
    Messages:
    49
    Thanks Received:
    0
    Location:
    Surrey
    Country:
    United Kingdom
    Hi ianblue

    Thanks for the info.

    Is 22mm just adequate or is it the correct size?

    I may as well lay the proper one while I am ripping the kitchen out!

    Thanks!
     
  10. Agile

    Agile

    Joined:
    26 Jun 2004
    Messages:
    64,020
    Thanks Received:
    4,591
    Location:
    London
    Country:
    United Kingdom
    I have not done the calculation. However, its does sound rather borderline. Particularly as actual pressure loss always ends up less than the calculated. Probably because the calculation assumes the pipe ends are deburred and reamed. If pipe slices are used then there is a reduction at every pipe entry to a fitting.

    My solution would probably to fit it in 28mm up to the cooker take off as thats more critical and is only a short distance. Of course every elbow has an effective length which means that section is equivalent to a much longer route.

    Get some other quotes and see what they tell you about upgrading the gas supply. Be wary of those who are not very concerned about that aspect of the installation.

    Tony
     
  11. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page