None of that surprises me, and I would be very surprised if the same was not true of the vast majority of electricians.It is a long time since I looked at those graphs in anger. ... But I have to admit in 30 years, I have never run an adiabatic for a ring final circuit.
However, we quite often see it being suggested that an 'adiabatic calculation is necessary', yet, without looking at such graphs (and understanding them more confidently than I do!), it's not possible to undertake a proper adiabatic calculation.
I can't find my 17th OSG, but I can't work out what is an equivalent Table in the 18th ed. one (there is no 'Table 2A') - what is the title of the Table?IIRC, it was realised circa 1977 (my memory may have it wrong) that you wouldn't get the correct disconnection times using 2.5/ 1.0 on a 3036. ... According to Table 2A in my 17th OSG, 2.5/ 1.0 will comply on a 32A MCB or 30A 1361 fuse, but not a 30A 3036. The quick fixes that were adopted (on Wylex Standard boards anyway) were either swapping out the 30A 3036 for a 20A 3036 or a 30A plug-in breaker.
Kind Regards, John