If the radiator has a specific flow and return as per
@just pumps then yes.
If the radiator is not flow specific and a TRV is fitted, it is usually fitted to the flow end, some TRV's can be used at either end, but some do have to be on the flow.
Also, is the lock shield valve fully open? It should be. The balancing rules applied to two pipe systems don't apply to one pipe systems.
However in general, one pipe systems are notoriously slow to heat up. The water is pumped around the one pipe loop, and it then relies on natural circulation of water (hot water rises, cooler water falls) for it to travel through the radiator. Because of this principle, the flow is pretty much the same through any radiator on a one pipe system, so larger radiators, especially doubles, sometimes don't get sufficient water through them fast enough to get them piping hot.
Unlike a two pipe systems where positive pressure from the pump is connected directly to the inlet and forces the water through the radiator, a one pipe radiator sits directly on top of the same pipe so the pressure from the pump that is exerted on the inlet and outlet are the same (apart from a tiny pressure drop produced by the section of pipe between the inlet and outlet) hence the slow flow.
The radiators at the furthest end from the boiler also receive cooler water as much of the heat will have already been removed by the previous radiators.