My mother has recently moved into a new build apartment block. The car park has pillar lights around the outside which is fed by two separate circuits. Recently one circuit started tripping the 30mA RCD the instant they were scheduled to turn on. After contacting the electrician for the development his solution was to remove the circuit from the RCD (leaving a large gap in the consumer unit where you touch the bus bar no problem!). When I asked him why he'd removed the RCD he cited that the outside lights have electronic ballasts which would always trip an RCD and it shouldn't have been put on it in the first place!
After he left, both circuits started tripping the 10A MCBs. He returned some weeks later and went though the wiring finding a non waterproof connection letting water in which caused the problem.
After finding the cause for the RCD and MCBs tripping he refused to put the circuit back on the RCD
As I understand, (from my rather limited knowledge) 17th edition regs require new installation to be protected from an RCD, is this not the case?
After he left, both circuits started tripping the 10A MCBs. He returned some weeks later and went though the wiring finding a non waterproof connection letting water in which caused the problem.
After finding the cause for the RCD and MCBs tripping he refused to put the circuit back on the RCD
As I understand, (from my rather limited knowledge) 17th edition regs require new installation to be protected from an RCD, is this not the case?