Overhead power supply to shed

Joined
18 Jul 2008
Messages
4
Reaction score
0
Location
Kent
Country
United Kingdom
just a quick question.

Am I ok to have a SWA cable or conduit ran overhead from the house CU to a shed CU. The distance is only about 2 metres and would save digging up the concrete floor.

Many thanks for replies in advanced.

Simon
 
Sponsored Links
Conduit should be heavy duty, and no joins.

SWA should be supported by a catenary wire, and/or supported so that there's no strain on the terminations.

Height AGL should be at least 5.3m if the position is accessible to vehicles (probably not), or otherwise at least 3m.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top