Hi everyone,

My boiler makes frequently loud noises


And often gives me the E133 and E119 errors; the first one goes away after resetting.

E133: Interruption Of Gas Supply or Flame Failure
E119: Low pressure/Water Pressure Switch Not Operated

I recall that the last winter I had to repressurize quite often but I do not seem to be able to find any leak and now it's been a while since I had that problem.

Problems usually start during the winter when I operate the central heating.

Any suggestion on what to try and investigate or what the problem might be?

Thank you
 
Looks like expansion vessel gone for starters

e133 is for a qualified engineer to investigate.
 
you need to repressurise the vessel outside the boiler and also the engineer needs to adjust/ replace the g valve as these are murder when starting up with that noise , also these valves are murder for letting by so contact an engineer . try turning the temp dial up to get rid of the noise for the time being or better still turn your boiler off to be on the safe side . actually done 3 in last 2 weeks
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.