Noticed the rads were boiling last night when they should have been off fiddled with the stat last night and nothing happened so looked at it in more details this morning and found the following:
When I turn the Honeywell room stat down, the flame symbol on the stats disappears and I hear a click I wait a few minutes at the boiler but I can still see the burner through the viewing hole burning bright.
Next I turn the HW and CH to off on the programmer, wait a few minutes at the boiler but I can still see the burner burning through the viewing hole.
Next I turn off the electric to the boiler, and programmer and everything shuts off. I give it a couple of minutes and turn the power back on. The boiler remains off
Next I turn the programmer to cont for both HW and CH and still the boiler remains off
Next I go to the room stat and turn this up until the flame symbol appears and I hear it click. I then watch the boiler and 20-30 seconds later it fires up
Next I go back to the room stat and repeat the first step but the boiler remains on
Guess at this stage i'm trying to narrow it down to either a boiler, room stat, or MV issue but not sure what process to check/follow next
Thanks for any help
When I turn the Honeywell room stat down, the flame symbol on the stats disappears and I hear a click I wait a few minutes at the boiler but I can still see the burner through the viewing hole burning bright.
Next I turn the HW and CH to off on the programmer, wait a few minutes at the boiler but I can still see the burner burning through the viewing hole.
Next I turn off the electric to the boiler, and programmer and everything shuts off. I give it a couple of minutes and turn the power back on. The boiler remains off
Next I turn the programmer to cont for both HW and CH and still the boiler remains off
Next I go to the room stat and turn this up until the flame symbol appears and I hear it click. I then watch the boiler and 20-30 seconds later it fires up
Next I go back to the room stat and repeat the first step but the boiler remains on
Guess at this stage i'm trying to narrow it down to either a boiler, room stat, or MV issue but not sure what process to check/follow next
Thanks for any help